Long story short, I replaced a draft inducer on a single phase rooftop furnace, and wired it exactly according to the printed wiring diagram which appeared both on the new inducer and the unit schematic . It had draft issues after I got done. Shop sent another another tech, and for "snicks and grins"
he reversed the wires on the draft inducer feeding power from l1 and l2, and leaving the lead to the capacitor where it was. This reversed the motor, creating a proper draft .
I never knew it was "that easy" to reverse a capacitor run motor...... Did he just get lucky, or will this always work?
I am attaching a diagram of the wiring diagrams for clarity
Howard
he reversed the wires on the draft inducer feeding power from l1 and l2, and leaving the lead to the capacitor where it was. This reversed the motor, creating a proper draft .
I never knew it was "that easy" to reverse a capacitor run motor...... Did he just get lucky, or will this always work?
I am attaching a diagram of the wiring diagrams for clarity
Howard