ATS schedule says 400A and draw out breaker say trip of 300A and frame indicates 400A.
You size conductors to the frame or trip setting?
ATS schedule says 400A and draw out breaker say trip of 300A and frame indicates 400A.
You size conductors to the frame or trip setting?
So you could set the trip to max @ 400A?Size per the drawings which should be sized per the trip setting. The frame is just the max rating of the device.
Sent from my iPhone using Tapatalk
So you could set the trip to max @ 400A?
They did. (2) sets 4/c #600 2 hour vitalink MC cable. Doesn't make sense.The engineer took the time to spec both frame size and trip setting, but they didn't size the wire?
Seems odd....
What's the diff between the two....adj trip or rating plug? ThanksIn my opinion it depends on if the breaker is an adjustable trip breaker and you set it down from 400 amps to 300 amps, or if you physically change a rating plug to change the trip point.
If it is adjustable trip, you apply the rules in 240.6(B) and (C).
If it has a rating plug to change the trip rating, then you treat it just like a 400 amp fusible disconnect with 300 amp fuses...you provide wire for 300 amps.
Take a look at those Sections in the NEC. One is restricted access, one is not.What's the diff between the two....adj trip or rating plug? Thanks
A rating plug is a physical change...you remove the 400 amp one and replace it with a 300 amp one.What's the diff between the two....adj trip or rating plug? Thanks
I doubt that this is really an adjustable trip breaker. Could just be a 300 amp breaker that is the size of a 400 amp frame.