Looking at another fraternity. Real basic, just a bunch of rooms with maybe a microwave plugged in and no central area with permanent provisions for cooking or anything. I'm guessing this is just a commercial motel and no afci rules applying. Am I correct ?
210.12(C) covers "Dormitory Units" and requires AFCI in same areas as in a dwelling unit.
I don't see anything in 406.12 that would require tamper resistant receptacles unless this dormitory does meet NEC definition of a dwelling unit, or is a dormitory for a child care facility.
240.24(B) may not require panels to be accessible to occupants if there is continuous maintenance services provided by building management.
It is completely new section in 2014. Here is what is says:I don't see a 210.12 (C) in my code book (2008) or the one being adopted in 6 months, (2011)
(C) Dormitory Units.
All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dormitory unit bedrooms, living rooms, hallways, closets, and similar rooms shall be protected by a listed arc-fault circuit interrupter meeting the requirements of 210.12(A)(1) through (6) as appropriate.
It is completely new section in 2014. Here is what is says:
OP needs to consider which code he is on when applying to his situation, as well as possibly determining if his application fits the NEC definition of a dwelling unit.It will be quite a while before many of us are using 2014.