Senior Member
- Location
- New York, 40.7514,-73.9925
When properly designing a single conductor layout in cable tray per 392.80(A)(2)(c), we use Table 310.15(B)(17) to determine the conductor ampacity. This is a 2000A feeder, so there is significant paralleled set reductions.
When these conductors enter a disconnect, where the conductor spacing cannot be maintained, is there any code relief to still allow the free air rating to be used for that short run into the enclosure? If not, it essentially will require the cable tray conductors to be reduced and have "normal" 310.15(B)(16) ampacities. An external splice at the enclosure from five sets (310.15(B)(16)) to three sets (310.15(B)(17)) is not practical.
When these conductors enter a disconnect, where the conductor spacing cannot be maintained, is there any code relief to still allow the free air rating to be used for that short run into the enclosure? If not, it essentially will require the cable tray conductors to be reduced and have "normal" 310.15(B)(16) ampacities. An external splice at the enclosure from five sets (310.15(B)(16)) to three sets (310.15(B)(17)) is not practical.