1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
I have a question about a free standing electric range/oven. Trying to calculate the appropriate wire and breaker size for this unit in a remodel. The nameplate reads 3 wire 120/240 14.1kW.
At 100% 14,100 / 240 = 58.75 This seems high to me.
I was looking over the Demand Factor table in 220.55 and I?m confused on which Demand Factor Column to use. If I use Column C, am I reading correctly -- at 8% + 10%, for the additional 2.1kW above the 12kW as in note 1.?
Any clarification will be greatly appreciated.
Norb
At 100% 14,100 / 240 = 58.75 This seems high to me.
I was looking over the Demand Factor table in 220.55 and I?m confused on which Demand Factor Column to use. If I use Column C, am I reading correctly -- at 8% + 10%, for the additional 2.1kW above the 12kW as in note 1.?
Any clarification will be greatly appreciated.
Norb