Freestanding outdoor GFCI

Status
Not open for further replies.

SparkyCAD

Member
Can I support an outdoor dupux GFCI receptacle (threaded entries) only with the two rigid conduits entering from one side?

If so, do I need to encase conduits in concrete for support?
 
See 314.23(F). The NEC does not mandate the use of concrete but it does state that the conduits must be secured within 18" of the enclosure.

Pete

Welcome to the forum:)
 
Thank you for your responses.

Thank you for your responses.

The installation is temporary (one year) and there will be limited access to the site.

If 12? to 18? above finished grade is secured then I am good.
 
FWIW, I would consider the conduits emerging from concrete encasement within 18" of the box "secured"

Pete
 