I had an after hours service call yesterday evening.
After two plug in space heaters were set to 'hi' home owner tripped a breaker.
Upon resetting breaker they were still without some power.
I get there and find two GFCI's tripped that are on completely unrelated circuits.
Bathroom one resets fine.
Kitchen one wont reset.
Its a 1969 house so some garage recepts are down stream of the kitchen GFCI.
I unplug the freezer and the GFCI resets.
I had an ideal 'sure test' with me.
All voltage readings normal, outlets are all grounded and have been replaced in the last 2 years.
I have a 3 prong to two prong adapter in my test bag, plug in freezer with adapter and GFCI holds.
I take the freezer plug off the GFCI test again this time measuring voltage from the frame ground to the ground pin on the outlet.
I get 57 volts.
I am still into this service call under 10 minutes.
This kitchen / garage circuit had nothing to do with the space heaters that tripped the breaker.
The name plate of the freezer says 5 amps, my ammeter is measuring about 8.
Why would a overload on a totally different circuit cause this?
After two plug in space heaters were set to 'hi' home owner tripped a breaker.
Upon resetting breaker they were still without some power.
I get there and find two GFCI's tripped that are on completely unrelated circuits.
Bathroom one resets fine.
Kitchen one wont reset.
Its a 1969 house so some garage recepts are down stream of the kitchen GFCI.
I unplug the freezer and the GFCI resets.
I had an ideal 'sure test' with me.
All voltage readings normal, outlets are all grounded and have been replaced in the last 2 years.
I have a 3 prong to two prong adapter in my test bag, plug in freezer with adapter and GFCI holds.
I take the freezer plug off the GFCI test again this time measuring voltage from the frame ground to the ground pin on the outlet.
I get 57 volts.
I am still into this service call under 10 minutes.
This kitchen / garage circuit had nothing to do with the space heaters that tripped the breaker.
The name plate of the freezer says 5 amps, my ammeter is measuring about 8.
Why would a overload on a totally different circuit cause this?