freezer

Status
Not open for further replies.
Re: freezer

I can't recall any minimum temperature limits in the NEC.

The internal wiring of a freezer, unless it's a walk in type, would't really be covered by the NEC anyhow.
 
Re: freezer

This is a large walk in spiral freezer it`s
20' high and 20' diameter.It also has 2 amonia evaperators with 3 7.5 hp. fans each.
 
Re: freezer

What code would govern the electrical eqipment
instalation of a freezer this size?
 
Re: freezer

A product standard from UL, perhaps appilances or freezers. You can download the UL General Product Listing Directory - White Book from this web site and propably find it there.
The NEC would cover the wiring to the freezer.
 
Re: freezer

The NEC certainly can and does apply to the wiring in coolers, freezers etc.

We are not talking about a simple appliance here, we are talking about something built on site, the NEC applies.

We have built cold storage warehouses bigger than 500,000 sq feet, the entire space was kept at -20 F.
 
Re: freezer

Originally posted by jy:
What code would govern the electrical eqipment
instalation of a freezer this size?
Wire it like you would any space.

It is common to use rain tight methods in freezers and coolers but that is not required.

One NEC rule that I urge you strongly to comply with is 300.7

300.7 Raceways Exposed to Different Temperatures.
(A) Sealing. Where portions of a cable raceway or sleeve are known to be subjected to different temperatures and where condensation is known to be a problem, as in cold storage areas of buildings or where passing from the interior to the exterior of a building, the raceway or sleeve shall be filled with an approved material to prevent the circulation of warm air to a colder section of the raceway or sleeve. An explosionproof seal shall not be required for this purpose.
If you ignore this you will have problems, condensate will collect in the boxes, raceways etc.

Every raceway that passes from the inside to the outside of the cooler needs to be sealed.

Duct seal can work, we often use silicone and some use spray foam.

You can check with the wire manufacturer's for recommended wire types.

We use THHN, remember you will not be installing it at -40F. Once it's in place and not being flexed the cold will not effect it.
 
Re: freezer

I agree with iwire,

I have had to go on a few service calls on walk in freezers where the conduit running into the freezer was not sealed, needless to say the switch directly below the conduit filled with condensate, froze, and shorted out.

Chris
 
Re: freezer

Thanks guys you`ve been a great help. But regretably we have 9 of these freezers that have been installed without the consideration of 300.7 and may take some time to fix.
 
Re: freezer

Originally posted by jy:
What type of wire do you use in a -40 deg.
spiral freezer?
I think you meant "What type of wire does my first year apprentice install in a -40 deg. freezer."

Steve
 