Okay, so this is arguably the simplest section of the NEC, however we have found away to argue it. I have interpreted 210.52(c) to mean that an island of 24" or greater that is at least 12" or deeper needs at least 1 receptacle. We have done it this way since the code was written. Now, an inspector in a city we don't normally work in has a "special" (IMHO) interpretation. So here is the actual code section.
At least one receptacle outlet must be installed at each island countertop space with a long dimension of 2 ft or more and a short dimension of 1 ft or more [210.52(C)This jurisdiction is saying that since the code uses the word "space" they interpret it to mean that all island spaces bigger than 24" need a receptacle. In other words, a 6' island needs 3 receptacles. There argument is that if it was intended that a counter of 24" OR MORE was to need only one receptacle it was say that explicitly. But since it says each counter SPACE of 24" or more, they intended it to be each 24". Any thoughts on how I can convince them? They brought this up on final, not rough-in.
At least one receptacle outlet must be installed at each island countertop space with a long dimension of 2 ft or more and a short dimension of 1 ft or more [210.52(C)This jurisdiction is saying that since the code uses the word "space" they interpret it to mean that all island spaces bigger than 24" need a receptacle. In other words, a 6' island needs 3 receptacles. There argument is that if it was intended that a counter of 24" OR MORE was to need only one receptacle it was say that explicitly. But since it says each counter SPACE of 24" or more, they intended it to be each 24". Any thoughts on how I can convince them? They brought this up on final, not rough-in.