Hello
I have a customer with a fryer that has a square-d 3-phase, 208volt, shunt trip breaker that trips as soon as you plug the receptacle into the outlet. This started after the cleaning person pressure washed the walls…. The cord, outlet and plug looks good (and dry) . Where the cord enters the fryer those terminations look good . The fryer technician says his end looks good. Could the shunt trip breaker be defective?
Thanks for the help.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
A shunt trip requires a control voltage to be applied. If the mechanism was faulty I don't think you would be able to reset the breaker.

If the breaker holds except when the fryer is plugged in, the problem is likely with the fryer
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
The shunt trip is likely triggered by the fire suppression system in the exhaust hood.

If it trips as soon as you plug in the appliance then something with the appliance is likely going on. Is it also a GFCI breaker? if so maybe moisture got somewhere it shouldn't be and is making enough of a ground fault to trip it? Otherwise most other conditions that would trip it would involve high enough current it likely arcs when plugging in as well.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Can you easily bypass whatever opens the circuit for the shunt to test it?
Temporarily disconnect the leads to the shunt trip module should accomplish this test, if it still trips it is not the shunt trip/or associated trip circuit.
 

Ravenvalor

Senior Member
If you look at the bottom of those 2 - dark lugs you can see burnt marks. The problem was inside the plug. Initially upon opening up the plug and inspecting the allen screw heads (and not the entire lugs) I did not see the problem. However when I removed the internal cover inside the plug (the cover that holds the 4 - lugs in place) I discovered where 2 - of the phase lugs were arcing. Not sure why but I can suppose that some strands from the cord conductors managed to touch each other. Either that or the 2 - lugs were arcing due to proximity. Maybe water got in there when the cleaner was pressure washing and that was the connection point but I did not see any moisture. Either way I learned a valuable lesson today, completely disassemble these plugs. :)

Thanks for the help.
IMG_6165.jpg IMG_6164.jpg
 