I'm trying to make sure that I'm understanding the disconnect requirement in article 514.
If I have a pair of fuel dispensers, each fed from its own single phase circuit. Can I use a pair of three pole disconnects just outside of the 20' classified area to disconnect all three conductors?
Or does it have to be a single disconnect?
514.11(C) indicates that "Emergency controls shall shut off all power to all dispensing equipment at the station."
Is it saying that one disconnect needs to be used to de-energize both dispensers at the same time, or that the controls just need to be capable of disconnecting both dispensers (ie. two switches would be fine).
Most likely I'm reading more into this than I need to.
Thanks.