I've wired plenty of permanent fuel storage tanks using explosion proof fittings, boxes and flex couplings but this projects has me asking a few questions. They will be storing gasoline and Diesel fuel in 3 tanks side by side. They are not bolted down and could be moved in the future. The units actually come with a 3 prong 6ft cord.
My thought was to run rigid conduit with boxes and proper fittings for Class1 divison 1 /2 and to drop a flexible cord off at each tank using Type TC-ER-HC cable with listed flex fittings. This would make it somewhat movable in the future without using explosion proof outlet boxes and cord ends. Am I on the right path or am I missing something? Thanks
My thought was to run rigid conduit with boxes and proper fittings for Class1 divison 1 /2 and to drop a flexible cord off at each tank using Type TC-ER-HC cable with listed flex fittings. This would make it somewhat movable in the future without using explosion proof outlet boxes and cord ends. Am I on the right path or am I missing something? Thanks