Most of the vid’s I’ve installed have a drive enable input. But this one doesn’t. The problem is, when power is removed for a period of time, the drive does not automatically restart, the run button on the drive has to be pressed to bring the drive back on line. This is a problem, because the drive is located in the control cabinet on a five ton bridge crane. I changed the trolley control to a freq drive because the trolley starts too quick, and swings the 3000 lb pallet of very breakable glass. The drive works perfectly other than having to restart it. They turn and lockout the crane to prevent unauthorized users from using it. I’ve went through the programming, and set everything the manual says to automatically enable it after power failure, but still does not automatically reset. Has anybody had this situation?