(My computer is so archaic that I have no way to turn the attached image right side up. Sigh!)
This building is in final stages of commissioning. The switchboard is installed and energized. Panel FPP feeds two fire pumps, one jockey pump, and two hangar bay doors. It gets its power from upstream of the main breaker, but apparently not in a separate vertical section. Also, a 100 amp feeder breaker would not hold indefinitely with locked rotor current from even one of the fire pumps, let alone both. I gather that since these pumps supplied expanding foam, and not fire water, they weren’t initially treated under article 695. I need to find a solution.
Here is what I hope can be done:
Do I have to abandon this scheme, and try to find a way to get the fire pumps each connected to a separate breaker upstream of the main and on a different vertical section than the main?
This building is in final stages of commissioning. The switchboard is installed and energized. Panel FPP feeds two fire pumps, one jockey pump, and two hangar bay doors. It gets its power from upstream of the main breaker, but apparently not in a separate vertical section. Also, a 100 amp feeder breaker would not hold indefinitely with locked rotor current from even one of the fire pumps, let alone both. I gather that since these pumps supplied expanding foam, and not fire water, they weren’t initially treated under article 695. I need to find a solution.
Here is what I hope can be done:
- Move the 100 amp feeder breaker into the vertical section that shows the SPD. If necessary, move the SPD to the vertical section that presently shows the breaker.
- Replace the 100 amp breaker with one that can handle locked rotor current from two fire pumps. Unless I can pin down the exact motor and its catalog data, I have to use 21 amp full load, times two motors, times 6, or 246 amps. I would use a 250 amp breaker.
- I believe I can leave the conductor sized for about 60 amps (2 motors at 21 amps, one of those with 25% extra, and one motor at 11 amps). I don’t have to size the feeder for the entire 250 amps. Is that right?
- I will also move the two hangar bay doors to another panel, to get them away from the fire pumps.
- The breakers on FPP that serve the two fire pumps are 35 amps. Do they also have to handle locked rotor current for their individual motor?
Do I have to abandon this scheme, and try to find a way to get the fire pumps each connected to a separate breaker upstream of the main and on a different vertical section than the main?