Hello all,
My company designs custom HVAC units that are designed to be used primarily for data centers. We have various designs of different products but for the most part, these units consist of a few motor pumps that pump water throughout some coils, and some EC fans that pull the air across the coils to chill the water inside the coils. There are several damper actuators and other sensors involved as well but those aren't really in question right now.
I am posting this question as this has got our Electrical engineering department divided right now. It is over the topic of how we are calculating the FLA of a custom HVAC unit. My question is, which FLA do we need to use in our load calculations for these units, the FLA of the VFD, or the FLA of the motor itself?
Traditionally, I have always calculated the FLA based on the nameplate data from the motor itself. The OCPD upstream of the VFD and the wire gauge is determined by the FLA of the VFD on the line side. However, some of the engineers I work with are stating that the FLA of the VFD is what should be used in the load calculations. The FLA then helps determine the MCA and the MOP of the units which is required by UL.
My concern with this is that we could potentially oversize the MCA and MOP and leave our electrical components susceptible to damage.
I have been told by a few of our engineers that supposedly this is a new standard to use the FLA of the “conversion device” (the VFD in this case) and not the FLA of the Motor. However, when I question them on this, they can not find the specific standard that states this. In all fairness, I can’t find anywhere that states the other side of the argument either.
If there is anything in the NEC, UL508A, UL1995, or 60335 that state the FLA of the VFD’s should be used, please help point me in the right direction so that we can reference one of these standards moving forward.
My company designs custom HVAC units that are designed to be used primarily for data centers. We have various designs of different products but for the most part, these units consist of a few motor pumps that pump water throughout some coils, and some EC fans that pull the air across the coils to chill the water inside the coils. There are several damper actuators and other sensors involved as well but those aren't really in question right now.
I am posting this question as this has got our Electrical engineering department divided right now. It is over the topic of how we are calculating the FLA of a custom HVAC unit. My question is, which FLA do we need to use in our load calculations for these units, the FLA of the VFD, or the FLA of the motor itself?
Traditionally, I have always calculated the FLA based on the nameplate data from the motor itself. The OCPD upstream of the VFD and the wire gauge is determined by the FLA of the VFD on the line side. However, some of the engineers I work with are stating that the FLA of the VFD is what should be used in the load calculations. The FLA then helps determine the MCA and the MOP of the units which is required by UL.
My concern with this is that we could potentially oversize the MCA and MOP and leave our electrical components susceptible to damage.
I have been told by a few of our engineers that supposedly this is a new standard to use the FLA of the “conversion device” (the VFD in this case) and not the FLA of the Motor. However, when I question them on this, they can not find the specific standard that states this. In all fairness, I can’t find anywhere that states the other side of the argument either.
If there is anything in the NEC, UL508A, UL1995, or 60335 that state the FLA of the VFD’s should be used, please help point me in the right direction so that we can reference one of these standards moving forward.