Full Size EGC

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Without know the circuit ampacity no one can say for sure if the EGC in the photo is larger than required or not. A 30 amp receptacle would have a full size EGC even if the ungrounded conductors were #6 AWG.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I follow the general rule that field-installed conductors need to be bushed, factory-installed don't.

Then there's AC/BX. :rolleyes:
 