Funny three way

Status
Not open for further replies.

andinator

Senior Member
Location
Lilburn Georgia
Let me preface this by saying I know this is a code violation. If I have a three way fed from one circuit and the neutral to a 60W keyless stolen from another circuit on the same leg of a single phase system, would the net result be .5A "added" to the neutral of circuit # two? Or would it be much worse than that. The neutrals of circuit # 1 are not attached to circuit # two at any point. Thanks
 

wbalsam1

Senior Member
Location
Upper Jay, NY
andinator said:
Nope. I know the code violation...I'm curious as to the additive effect. I've already got it worked out in my pea size brain.:grin: Thanks.

Same phase or opposing? :smile: Oops, sorry, I just saw you said same leg. Seems to me that it would only add the load it's phase conductor was serving, namely .5 amps.
 
Last edited:

brian john

Senior Member
Location
Leesburg, VA
You increase the EMF around both set of cables, other than that the system will work, it had better I see this all the time that is Neutral current where it does not belong.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
andinator said:
The neutrals of circuit # 1 are not attached to circuit # two at any point. Thanks

Brian is correct that there will be an increae in EMF's, however the increase would be pretty insignificant with a 60 watt bulb.

The bigger issue I see is if someone turns off the breaker on circuit #2 then lifts the neutral from the neutral buss. If that 60 watt bulb is on it will be sending current back through that neutral and becoming a potential shock hazard for the poor electrician at the panel. He would not be expecting that one, for sure.
 