NegPF
New User
- Location
- Milford PA
- Occupation
- Mechanical Engineer
I have a furnace that calls for 15 AMPS MCA, but a minimum and max overcurrent protection device of 20 amps. The builder installed a 15 amp breaker with 14/2 wiring. I asked them to swap it to a 20 amp breaker with 12/2 as the manufacturer states it wants a minimum of a 20 amp breaker, but builder is pushing back that MCA is 15 amps, so what is installed in fine. He states that electrical inspector passed it, so its fine. He also did something similar with condensing unit, unit has MCA of 26 but minimum breaker of 35 and max of 45, but has it with 10/3 wiring on 30 amp breaker, i asked them to atleast change the breaker to 35 or 40. Does this sound right?
It is a 1001521SA furnace.
It is a 1001521SA furnace.