A wiring scheme for a furniture system calls for 3 circuits from one panel and 1 circuit from another panel. How do you go about disconnecting power to all circuits to work on the furniture system?
How would you know the furniture is fed from 2 panels then? Is there a labeling requirement at the breakers or at the furniture?
605.7 Freestanding-Type Partitions. Partitions of the
freestanding type (not fixed) shall be permitted to be connected
to the building electrical system by one of the wiring
methods of Chapter 3. Multiwire branch circuits supplying
power to permanently connected freestanding partitions
shall be provided with a means to disconnect simultaneously
all ungrounded conductors at the panelboard where
the branch circuit originates.
how would you know where to disconnect the power if it was only one one panel?
i don't think any of this stuff about MWC has anything to do with the OP's question about running circuits from multiple panelboards.
Just curious, even though the furniture manufacturer wiring CAN accommodate 3 circuits from 1 panel and another circuit from another panel, doesn't mean you MUST wire it that way correct?
Meaning, why not just take that extra circuit out of the original panel and call it a day? Circuits, 1,3,5,7. Who's to say that if 7 is fed from another panel it does anything different?