I've made this post before, but rather than refer to that post, it's easier for me to just reiterate.
An unfused disconnect is only good for 10,000 amps withstand. So, if the available fault current exceeds 10kA, then the manufacturer of the disconnect must be the same manufacturer of the upstream OCPD, since that would be a listed combination - or use a fused disconnect with appropraitely applied fuses.
Personally, an unfused disconnect is always my first choice, since I think it's an unnecessary addition of a failure point. But you have to look at the fault current situation as described above.
JM