I need to tap off a 2500A generator bus for 100A of lighting and receptacle power. The closest place I have for a disconnect is about 35 feet away, so I can't legally use unfused tap conductors.
There is an empty compartment above the generator ACB cubicle that contains some instrument transformers and low voltage terminal strips. Any code conflicts with putting a 600V 3P fuse block in there?
This is utility owned equipment, but we're the utility, so no worries there.
Thanks.
-John
There is an empty compartment above the generator ACB cubicle that contains some instrument transformers and low voltage terminal strips. Any code conflicts with putting a 600V 3P fuse block in there?
This is utility owned equipment, but we're the utility, so no worries there.