Fuse blown, but still allowing current on the load side?!

zappy

Senior Member
Location
CA.
I was troubleshooting a 480V heater in our paint shop. I was checking the fuse disconnect for voltage. Line side 277V to ground on all three phases. Line side A to B, A to C, B to C 480 V. Okay so the load side, 277 V on all three phases. Load side A to B 480V, A to C 0V, B to C 480V. So somethings not right, so I pulled the fuses out and I checked them. Fuse A was bad. So how did I get 277 V to ground??? Maybe somebody else has experienced this before. Thank you for your help.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I was troubleshooting a 480V heater in our paint shop. I was checking the fuse disconnect for voltage. Line side 277V to ground on all three phases. Line side A to B, A to C, B to C 480 V. Okay so the load side, 277 V on all three phases. Load side A to B 480V, A to C 0V, B to C 480V. So somethings not right, so I pulled the fuses out and I checked them. Fuse A was bad. So how did I get 277 V to ground??? Maybe somebody else has experienced this before. Thank you for your help.
Saw it all the time in old fuse panels where one of the mains blew.

Yes, misleading.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I have also done that with a test light. If it lights, the fuse is blown.
I use my K-60 for 99% of my troubleshooting.

Years ago, someone asked me what stops the current of the load from blowing up the tester.

I had to ask him what stops that from happening on a line-to-line test for it to dawn on him.
 
Top