Fuse blown, but still allowing current on the load side?!

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
I was troubleshooting a 480V heater in our paint shop. I was checking the fuse disconnect for voltage. Line side 277V to ground on all three phases. Line side A to B, A to C, B to C 480 V. Okay so the load side, 277 V on all three phases. Load side A to B 480V, A to C 0V, B to C 480V. So somethings not right, so I pulled the fuses out and I checked them. Fuse A was bad. So how did I get 277 V to ground??? Maybe somebody else has experienced this before. Thank you for your help.
 
I was troubleshooting a 480V heater in our paint shop. I was checking the fuse disconnect for voltage. Line side 277V to ground on all three phases. Line side A to B, A to C, B to C 480 V. Okay so the load side, 277 V on all three phases. Load side A to B 480V, A to C 0V, B to C 480V. So somethings not right, so I pulled the fuses out and I checked them. Fuse A was bad. So how did I get 277 V to ground??? Maybe somebody else has experienced this before. Thank you for your help.
Saw it all the time in old fuse panels where one of the mains blew.

Yes, misleading.
 
I have also done that with a test light. If it lights, the fuse is blown.
I use my K-60 for 99% of my troubleshooting.

Years ago, someone asked me what stops the current of the load from blowing up the tester.

I had to ask him what stops that from happening on a line-to-line test for it to dawn on him.
 