Is there any reason that all fuses in a facility would need to be the same manufacturer. A customer of ours is being told that it would cause problems
Short answer is "No".Is there any reason that all fuses in a facility would need to be the same manufacturer. A customer of ours is being told that it would cause problems
That said, below 0.01 is sub one-cycle. So this may or may not be of concern for you.
But it occurs whenever the fault current exceeds the 0.01 sec crossing point for the fuse curve. Which is not unreasonable to happen, with smaller fuses (200A and smaller) and large available fault currents.