I have an inspection where the contractor is attempted to reduce a 42K SCA to supply equipment with a 5K SCCR. The supply is 400 amps.
Ignoring wire length, etc for conversatuon sake, is there a 400 amp fuse that will reduce 42 to 5 ?.
I've not found one.
I have a similar situation on my job.
There is one manufacturer that makes HVAC equipment has a higher rating than 5K. All others are 5K.
My confusion is this. And please enlighten me because my understanding is far less than I am comfortable with on this subject:
article 110.9 of the NEC requires overcurrent protective devices to have interrupting ratings sufficient for the available fault current and voltage at the equipment it is intended to
protect. According to Littlefuse.
So you need to know the let through current of a fuse or a breaker, yet the fuses and breakers tell you the maximum interrupt rating and the higher the interrupt rating the less let through there is. They don't tell you the let through current. So, if I have a 65KAIC breaker in a switchboard 100 feet away from the equipment, how does one ( especially the average electrician, maintenance person or inspector even determine what the actual available current will be at a piece of equipment that has say a 5K SCCR? more so, allegedly a 65KAIC breakers let's less current through than a 22KAIC breaker. How much less? Where is this information? They talk about current limiting breakers and fuses, but I don't see where it actually says how much current it limits. Before I started trying to wrap my limited brain around it, I thought that the 65KAIC meant something regarding the current limiting. How?
Lastly, please tell me if I simplistically understand the issue:
My assumption is that a piece of equipment or feeder wire, can sustain a certain amount of current for a certain amount of time before bursting in to fire with threat to others. The breaker or fuse must disconnect before this current before that time is exceeded.
SCCR and AIC deal with instantaneous trip which is in fact not instantaneous, but as close as currently possible with technology.
Say a 10 KAIC breaker is subject to 25KAIC, then it would fuse together in an "instant" situation thereby letting the 25KAIC through so we must depend on a large KAIC breaker up stream interrupt this current before it burns things up. Thereby, coordinated tripping. Not to be confused with selective tripping where a coordination study determines that a downstream breaker is given the time to clear a fault more quickly than a larger upstream breaker.
The entire system being designed to interrupt the maximum let through of the power source (transformer, generator etc.) before it saturates or burns up.
So given all of this, how does the breaker limit the amount of current available at a piece of equipment?
Sorry if this commandeers your question Augie, but I have had this on my list of things to do and I think the answers may be an in depth answer to your more specific question.