Guide to Ampere Ratings, As taken form Eaton C-H
?E? Designation: Fuses rated 100E or below will melt in 300 seconds at a current value between 2.0 and 2.4 times the E number. Fuses rated above 100E will melt in 600 seconds at a current value between 2.2 and 2.64 times the E number. If the current is higher than 2.4 or 2.64 times the E number, the user must consult the time-current curves for that particular fuse.
?R? Designation: The fuse will melt in 15 to 35 seconds when the current equals 100 times the R number. If the current is higher than 100 times the R number, the user must consult the time-current curves for that fuse.
?C? Designation: The fuse will melt in 1000 seconds at a current value, between 1.7 and 2.4 times the C number.
If the current is higher than 2.4 times the C number, the user must consult the time-current curves for that particular fuse.
?A? Designation: Fuses that do not comply with ?E?, ?R?, or ?C? designations.
Expulsion fuses can also be E-rated, K-rated and T-rated, and are also covered in the ANSI standards. The K and T ratings refer, respectively, to relatively ?fast? and ?slow? melting expulsion fuses. Detailed time-current tables would be needed to adequately define the ratings.