I have googled this question and really didn't get a clear answer.

What is (if any) the difference bettween FLN-R fuses and FRN-R?
Which type should I be using for a service disconnect?
Thanks!
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
The "R' stands for rejection type

I believe they are the same just different manufacturers FRN-R is cooper/bussmann and FLNR is Littlefuse but you will need to check the performance curves
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The "R' stands for rejection type

I believe they are the same just different manufacturers FRN-R is cooper/bussmann and FLNR is Littlefuse but you will need to check the performance curves

Yes, those are just brand name differences in nomenclature for the same fuse. Both are what's called a "Class RK-5" time delay fuse, meaning they are rated for 200kAIC @ 240VAC, perfect for use in Service Disconnects.
 