Hi guys, what is the minimum fuse size for a 50hp fire pump required by NEC? is it FLAX250% OR 300% OR even 600%??
that means 600%? This is too much..From what I can recall, the you are supposed be able to carry locked rotor current indefinitely.
could be less then 600. There is a difference between peak inrush when first energizing and locked rotor - locked rotor already has established fields but draws a heavy current because there is no rotation.that means 600%? This is too much..
that means 600%? This is too much..
could be less then 600. There is a difference between peak inrush when first energizing and locked rotor - locked rotor already has established fields but draws a heavy current because there is no rotation.
Source and circuit impedance can impact both these figures also.
The concept with fire pumps is if the building is already on fire we don't care if the pump motor burns out - we want it to deliver whatever it can as long as it can.
It still needs short circuit and ground fault protection though.
If you are unsure, we are not the place to grant you permission, we can only suggest. The correct answer was given and is that the fuse must be sized to provide Locked Rotor Current indefinitely. We are not there to read the motor nameplate, but as a GENERALIZATION, the LRC will be 600% of FLA. So get the FLA of your motor, multiply it by 6 and call it a day.It is ok If I make 400as/af for 50 hp fire pump?
Interesting to cogitate on that one.If you are unsure, we are not the place to grant you permission, we can only suggest. The correct answer was given and is that the fuse must be sized to provide Locked Rotor Current indefinitely. We are not there to read the motor nameplate, but as a GENERALIZATION, the LRC will be 600% of FLA. So get the FLA of your motor, multiply it by 6 and call it a day.
When you say "This is too much!", you have to keep in mind the over-arching principal on all things related to Fire Pumps:
"Run To Destruction".
Interesting to cogitate on that one.
Could the motor withstand locked rotor current indefinitely?
Is it designed to meet that requirement?
Maybe a non-standard rotor could be used to limit the LRC to much less than 600%.
One other point. If it really is a locked rotor, the pump won't pump anything which would render it ineffective as a fire pump.
Just my idle thoughts over a glass of Merlot............:thumbsup:
It is ok If I make 400as/af for 50 hp fire pump?
My question to you would be why are you putting an OCPD ahead of the fire pump controller at all. While it can be done, and in some install scenarios required, most garden variety installs of a fire pump this size the most common method would be to run the service conductors directly from the POCO to the controller.
I don't suppose you can here either.Over here you can't just slap a motor onto a pump and call the combination a fire pump.
Hi guys, what is the minimum fuse size for a 50hp fire pump required by NEC? is it FLAX250% OR 300% OR even 600%??
I have seen so many 75 hp fire pumps only using 800amp breakers. I am just curious. We shall have about 211 amp FLA for 75 hp fire pump. In this case, we should use fuse size which over 1200 amp in accordance with the NEC code relate to locked-rotor current.
Correct me if i am wrong. i really appreciate it. I am still learning..
I have seen so many 75 hp fire pumps only using 800amp breakers. I am just curious. We shall have about 211 amp FLA for 75 hp fire pump. In this case, we should use fuse size which over 1200 amp in accordance with the NEC code relate to locked-rotor current.
Correct me if i am wrong. i really appreciate it. I am still learning..
what voltage? 208/3 ?
fla = 211 ?
or lra?
yes, 208v/3 phase