fuse size for fire pump

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
that means 600%? This is too much..
could be less then 600. There is a difference between peak inrush when first energizing and locked rotor - locked rotor already has established fields but draws a heavy current because there is no rotation.
Source and circuit impedance can impact both these figures also.

The concept with fire pumps is if the building is already on fire we don't care if the pump motor burns out - we want it to deliver whatever it can as long as it can.

It still needs short circuit and ground fault protection though.
 

defishu

Member
Location
new york
could be less then 600. There is a difference between peak inrush when first energizing and locked rotor - locked rotor already has established fields but draws a heavy current because there is no rotation.
Source and circuit impedance can impact both these figures also.

The concept with fire pumps is if the building is already on fire we don't care if the pump motor burns out - we want it to deliver whatever it can as long as it can.

It still needs short circuit and ground fault protection though.

It is ok If I make 400as/af for 50 hp fire pump?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It is ok If I make 400as/af for 50 hp fire pump?
If you are unsure, we are not the place to grant you permission, we can only suggest. The correct answer was given and is that the fuse must be sized to provide Locked Rotor Current indefinitely. We are not there to read the motor nameplate, but as a GENERALIZATION, the LRC will be 600% of FLA. So get the FLA of your motor, multiply it by 6 and call it a day.

When you say "This is too much!", you have to keep in mind the over-arching principal on all things related to Fire Pumps:

"Run To Destruction".
 

Besoeker

Senior Member
Location
UK
If you are unsure, we are not the place to grant you permission, we can only suggest. The correct answer was given and is that the fuse must be sized to provide Locked Rotor Current indefinitely. We are not there to read the motor nameplate, but as a GENERALIZATION, the LRC will be 600% of FLA. So get the FLA of your motor, multiply it by 6 and call it a day.

When you say "This is too much!", you have to keep in mind the over-arching principal on all things related to Fire Pumps:

"Run To Destruction".
Interesting to cogitate on that one.
Could the motor withstand locked rotor current indefinitely?
Is it designed to meet that requirement?
Maybe a non-standard rotor could be used to limit the LRC to much less than 600%.
One other point. If it really is a locked rotor, the pump won't pump anything which would render it ineffective as a fire pump.

Just my idle thoughts over a glass of Merlot............:thumbsup:
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Interesting to cogitate on that one.
Could the motor withstand locked rotor current indefinitely?
Is it designed to meet that requirement?
Maybe a non-standard rotor could be used to limit the LRC to much less than 600%.
One other point. If it really is a locked rotor, the pump won't pump anything which would render it ineffective as a fire pump.

Just my idle thoughts over a glass of Merlot............:thumbsup:

Over here you can't just slap a motor onto a pump and call the combination a fire pump. Motors for fire pumps must be listed to UL 1004-5, the pumps are listed to UL 448 (centrifugal), the controllers to UL 218, etc.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It is ok If I make 400as/af for 50 hp fire pump?

My question to you would be why are you putting an OCPD ahead of the fire pump controller at all. While it can be done, and in some install scenarios required, most garden variety installs of a fire pump this size the most common method would be to run the service conductors directly from the POCO to the controller.
 

Ingenieur

Senior Member
Location
Earth
695.4.B.2
> LRC of pump + LRC booster pump + FLC of all other connected devices

must be a listed device for a fire pump controller assy and carry FLC x 600% for 2 minutes
must withstand 24 x FLC upon a restart transient
carry 300% x FLC for 10 min
trip point non-filed adjustable
 

Ingenieur

Senior Member
Location
Earth
My question to you would be why are you putting an OCPD ahead of the fire pump controller at all. While it can be done, and in some install scenarios required, most garden variety installs of a fire pump this size the most common method would be to run the service conductors directly from the POCO to the controller.

:thumbsup:

no CB until the rated/listed controller CB
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is this in NYC? If so you should check the NYC electrical code there are some significant changes from the NEC requirements.
 

defishu

Member
Location
new york
Hi guys, what is the minimum fuse size for a 50hp fire pump required by NEC? is it FLAX250% OR 300% OR even 600%??

I have seen so many 75 hp fire pumps only using 800amp breakers. I am just curious. We shall have about 211 amp FLA for 75 hp fire pump. In this case, we should use fuse size which over 1200 amp in accordance with the NEC code relate to locked-rotor current.


Correct me if i am wrong.
i really appreciate it. I am still learning..
 

Ingenieur

Senior Member
Location
Earth
I have seen so many 75 hp fire pumps only using 800amp breakers. I am just curious. We shall have about 211 amp FLA for 75 hp fire pump. In this case, we should use fuse size which over 1200 amp in accordance with the NEC code relate to locked-rotor current.


Correct me if i am wrong.
i really appreciate it. I am still learning..

what voltage? 208/3 ?
fla = 211 ?
or lra?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I have seen so many 75 hp fire pumps only using 800amp breakers. I am just curious. We shall have about 211 amp FLA for 75 hp fire pump. In this case, we should use fuse size which over 1200 amp in accordance with the NEC code relate to locked-rotor current.


Correct me if i am wrong.
i really appreciate it. I am still learning..

You don't look to the NEC for the locked rotor current value. You go to NFPA 20.
 

kwired

Electron manager
Location
NE Nebraska
Use of listed fire pump controller will likely already have whatever is needed if it is properly matched to the fire pump. All you need to do is properly size the conductors to it. Make sure the supply side is service conductors.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
yes, 208v/3 phase

Then per NFPA 20-2013 9.5.1.5, multiply the previous value I gave of 362 by the ratio of 460/208 which gives you 800.58 amps. Your disconnect, fused or unfused, must be rated for this locked rotor current.
 