Greetings,
I am trying to determine how to size a set of primary fuses in a load break switch which will be feeding (3) loop fed 2500KVA transformers. It is considered an unsupervised location. NEC tells me maximum 300% of transformers rated current but that would be for a single transformer. I will be feeding 3 of them from the same switch. The utility company primary is 12,470V. I am likely getting into the need for a MV metal clad circuit breaker instead of fuses for proper coordination with the fuses in the transformer and with the utility company's upstream protection but I am still interested in how this is accomplished.
Thank You in advance for your interest and responses.
I am trying to determine how to size a set of primary fuses in a load break switch which will be feeding (3) loop fed 2500KVA transformers. It is considered an unsupervised location. NEC tells me maximum 300% of transformers rated current but that would be for a single transformer. I will be feeding 3 of them from the same switch. The utility company primary is 12,470V. I am likely getting into the need for a MV metal clad circuit breaker instead of fuses for proper coordination with the fuses in the transformer and with the utility company's upstream protection but I am still interested in how this is accomplished.