I am on a job where we have a group of existing heat pumps that need to be checked for proper installation. The manufacturers name plate states that the maximum time delay fuse or HACR C/B allowed is 15A, however, upon opening the discos we found that they were fused with 20A time delay fuses. It is my understanding that, ideally, the disco should be fused in accordance with the pumps FLA and should not exceed the maximum fuse allowed by the manufacturer. Our plan was to swap out all the 20A fuses with new 15A fuses, and all the 30A fuses with 25A fuses (there are several heat pumps with max allowable fusing at 25A). Does anyone see where this might be an issue? Are we correct in assuming that they should be changed? Motors and HVAC are not my strong suit and i would appreciate any feed back.
Also, FYI, the branch circuit is sized correctly and is protected up to the disco accordingly, that is 20A C/B for #12 and 30A C/B for #10. Also, the units have no integral fuses or OL protection that we can see.
Thank you again.
God bless.
Also, FYI, the branch circuit is sized correctly and is protected up to the disco accordingly, that is 20A C/B for #12 and 30A C/B for #10. Also, the units have no integral fuses or OL protection that we can see.
Thank you again.
God bless.