If you have a fused disconnect that is acting as a branch overcurrent device, how do you size the fuse based on all of the loads involved? I have a control panel where we have a few motor and non-motor loads in a single branch circuit. I have to size the main panel disconnect fuse size but this would be sizing as a branch overcurrent device, I think.
Consider the following as components of a single branch circuit, the total load is 134A
Consider the following as components of a single branch circuit, the total load is 134A
- 1 100HP VFD, 124FLA - there is no branch circuit protection provided, max per documentation is 200A fuses (no minimums listed), and this I'm hoping can be covered by the main disconnect
- 2 Motors, 2HP, 3.4FLA, each protected by an MPCB set at 3.4A
- 1 1000VA 480x120 single phase transformer protected by its own 4A breaker, 2.1FLA
- 1 480Vac to 24Vdc power supply protected by its own 10A breaker, 0.9FLA