Fuse sizing
kjroller
Dawson Mn
Master electrician
Not doing this but just for my knowledge I am wondering how to size a fuses for a disconnect. Lets say 100 amp service needs fusing. How would I calculate this versus a breaker I know how to size a breaker but are fuses different? I also know how to size fuses for a motor but just wondering for a situation like the one above how they are sized
For a service the OCPD, whether as a fuse or as a circuit breaker would be the same size.
100 amp service would get 100 amp fuses.
So the rule of 80 or in this case 83% load since its a feeder so i could use 83 amps on a 100 amp fuse ?
If you actually have a continue 100A load you would use 125A OCPD (fuses or breaker) and 125A conductors.
If you have an article 220 calculation for a residence that comes to 100A you use 100A OCPD and 83A conductors.
There is no 83% load rule but you are allowed to use conductors sized at 83% of the size of the OCPD due to load diversity on the service.
So instead lets say it draws 100 amps in that case I would need 125 amp fuse
You can size the service based on the load calculation if it comes out to 100 amps then you can use a 100 amp OCPD.
Question then isnt it good practice to try to keep your breaker at 80% of the current rating or does service calc take that into account when you calc a 100 amps for load and use 100 amp breaker?
No need to worry about 80% because the load calculation has taken that into account.
So in other words use service calc for exact amperage on main OCPD but on a branch circuit only load to 80%.
Enclosed OCPD have the same limitations whether they are fuses or breakers. Continuous loading, at 100%, can only occur for 3 hours.