Morning guys
I got 400 amp fused disco on a chiller. My problem is I think the cutler-hammer slide in style fuse clips are sprung and when I draw my FLA for extended periods I'm generating a lot of heat at the connection point and blowing my fuse... not through an overcurrent situation but a thermal situation from the ambient area around the fuse clip itself. I had my power monitoring equipment on for the W/E and this never shows a over current event. I dont have a way to record temp over time though.
I'm wondering if there is a style of fuse at the 400 amp level which does'nt have the thermal feature included. I'm useinf a FRN-R-400 now and I dont think I need this. Eventually I'll have to replace the clips or the whole disco with somthing else.
What do you guys think... Does a fuse like this exist.
Thanks
Steve
I got 400 amp fused disco on a chiller. My problem is I think the cutler-hammer slide in style fuse clips are sprung and when I draw my FLA for extended periods I'm generating a lot of heat at the connection point and blowing my fuse... not through an overcurrent situation but a thermal situation from the ambient area around the fuse clip itself. I had my power monitoring equipment on for the W/E and this never shows a over current event. I dont have a way to record temp over time though.