Owing to the extremely low SCCR rating of unfused disconnect switches (something like 7,500A, we routinely “own” fuses (assuming 480V) to eliminate the concern.
The contractor on a recent project came back asking for a type fuse. Even when no other contractor has come back to me with this quesstion, it's nevertheless a fair one.
Given that the disconnect is sized for 125% of FLA (and then next standard size up) and that the OCP upstream could be anything up to 250%, I imagine the answer is that these should be 125% FLA (and next size) but that they should provide short circuit protection only; no overload capability.
The contractor on a recent project came back asking for a type fuse. Even when no other contractor has come back to me with this quesstion, it's nevertheless a fair one.
Given that the disconnect is sized for 125% of FLA (and then next standard size up) and that the OCP upstream could be anything up to 250%, I imagine the answer is that these should be 125% FLA (and next size) but that they should provide short circuit protection only; no overload capability.
- Do you agree with that and
- What type fuses should I be specifying?