Is there a restriction in the Code that does not allow Fused and Non-Fused conductors occupying the same wireway or conduit without separation or barrier partitions?
I gather from your answer that if the secondary conductors coming from the service transformer are occupying the same wireway that these fused feeder conductors, then this is a violation. I would need to install some sort of divider to separte the two different conductors.
Correct, conductors other than service conductors shall not be installed in the same service raceway or service cable.
A wireway is a raceway.