I received a submittal that showed a fused disconnect at an AHU. I had spec'd a non-fused disconnect in this location due to the disconnect being needed for disconnecting means only and not over-current protection. When we questioned the manufacturer they said this:
"for code and service purposes we have a dual disconnect system. One circuit breaker inside the control panel and a fused arc flash disconnect on the outside. We need the fused disconnect to be able to service without the full protective clothing requirement."
Now am I missing something here? It is my understanding (and has been for a long time) that there is no code requirement for OCP at equipment. I'm pretty sure the manufacturer is wrong regarding the code requirement, but regardless if it's in the instructions it would fall under 110.4 (B) anyway. Thoughts?
Thanks,
-Drew
"for code and service purposes we have a dual disconnect system. One circuit breaker inside the control panel and a fused arc flash disconnect on the outside. We need the fused disconnect to be able to service without the full protective clothing requirement."
Now am I missing something here? It is my understanding (and has been for a long time) that there is no code requirement for OCP at equipment. I'm pretty sure the manufacturer is wrong regarding the code requirement, but regardless if it's in the instructions it would fall under 110.4 (B) anyway. Thoughts?