Fused Disconnect Mounted in Unit Ventilator

Status
Not open for further replies.

DJordan23

Member
Location
Waterloo, IA
Occupation
Electrical Engineer
Would the installation of a fused disconnect that serves as an overcurrent protection and disconnecting means inside a unit ventilator as long as the access door only requires the use of a key be acceptable?

Referencing 440.14 Location, 240.24 Location in or on premises and definition of readily accessible.

Thanks!
 
Welcome to the forum.

I believe a disconnect must be externally accessible, requiring no keys or tools.
 
Perhaps I don't understand "inside a unit ventilator" but if there is air flow it seems a possible violation of 300.22
 