Would the installation of a fused disconnect that serves as an overcurrent protection and disconnecting means inside a unit ventilator as long as the access door only requires the use of a key be acceptable?

Referencing 440.14 Location, 240.24 Location in or on premises and definition of readily accessible.

Thanks!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

I believe a disconnect must be externally accessible, requiring no keys or tools.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Perhaps I don't understand "inside a unit ventilator" but if there is air flow it seems a possible violation of 300.22
 