I apologize for another long post some replies need explanation.
"I have heard CB's (big ones) need to be recertified/recalibrated by the factory after a certain amount of trips."
Really?
Have you had an opportunity to review the testing requirement that are required to be UL489 listed?
When a fuse blows it commonly is only one leaving the other two. Now you have a single phasing event that could damage the equipment.
Then it is going to the store room the get a replacement fuse. Replace the fuse and cross you fingers that it holds. If not hopefully you have another and fuses may not be cheep either.
Then, why did the fuse blow, short circuit or overload?
With a breaker it can be reset by latching to the off position and then closing it. And if u you happen to be standing there when it trips if the breaker is able to be latched right away the cause of trip is probably instantaneous as a result of a fault. It is not a good practice to close the breaker until the cause of the fault is resolved. Would it be a pleasent thing to do with a fused disconnect by replacing the fuse and the closing the switch back into a fault?
With a breaker by needing to wait a bit before the breaker can be latched is a good indicator that the thermal elements need no cool some which is an indicator of an overload.
A worst case scinereo is a bolted fault which are very rare where arcing faults are a more common.
And, if you question a breaker, breakers can the tested to varify their integrity. Try that with a fuse. You just hope that the fuse does what it is supposed to do.
A common breaker interupts in less than a 1/2 cycle. A current limiting breaker must limit the let through current it 1/4 cycle or less, time after time.
At what point does a fuse element start to clear and then completely clear? With a breaker hit the trip bar and it's less than a 1/2 cycle regardless.
There no magic with solid state trip units either other than features as they have to hit the trip bar the same as the thermal mag breakers and are no faster and require no addition maintenance.