I've been out of school for a year now, and the more I learn, the more questions I have. I am currently doing consulting work in Florida.
The engineers I work under like to use a fused disconnect as a local means of disconnect, for motor driven devices. We may also use a combination starter/disconnect. I have been told that fuses will provide better protection for the equipment, usually an air handler.
A typical circuit would involve a breaker in the panelboard, wire sized to the breaker, a local fused disconnect, a starter provided by the equipment manufacturer and the equipment.
The starter should provide overload protection to the motor, the breaker should protect the wire, and a nonfused disconnect would provide a local means of disconnect.
Now, does using a fused disconnect present an additional risk in a multi-phase circuit? If a fuse for Phase A opens that phase and Phase B and C are still closed, does it single phase the motor? (I'm not sure if that is the right terminology.) Would that cause more damage? If a breaker was the only overcurrent protection, all 3-phases should open.
Thanks for the help.
The engineers I work under like to use a fused disconnect as a local means of disconnect, for motor driven devices. We may also use a combination starter/disconnect. I have been told that fuses will provide better protection for the equipment, usually an air handler.
A typical circuit would involve a breaker in the panelboard, wire sized to the breaker, a local fused disconnect, a starter provided by the equipment manufacturer and the equipment.
The starter should provide overload protection to the motor, the breaker should protect the wire, and a nonfused disconnect would provide a local means of disconnect.
Now, does using a fused disconnect present an additional risk in a multi-phase circuit? If a fuse for Phase A opens that phase and Phase B and C are still closed, does it single phase the motor? (I'm not sure if that is the right terminology.) Would that cause more damage? If a breaker was the only overcurrent protection, all 3-phases should open.
Thanks for the help.