Hello,
There has been some debate in our office on this subject. The scenario is we have 200 Amp breaker on the first floor feeding a 112kva transformer on the 3rd floor. The transformer then feeds a panel with a MCB. The calculated available fault current at the primary side of the transformer on the third floor is approximately 60kaic. We have a disconnect switch on the primary side of this 3rd floor transformer. Question, is the disconnect required to be fused to meet the AIC rating of the circuit it's on? My understanding is that an unfused disconnect is only rated 10kaic. The answer seem to be obviously Yes you need a fuse, but I'm receiving some push back. We meet the OCPD for the transformer from the breaker, but if a fault occurs it could potentially damage that disconnect. Am I missing something?
There has been some debate in our office on this subject. The scenario is we have 200 Amp breaker on the first floor feeding a 112kva transformer on the 3rd floor. The transformer then feeds a panel with a MCB. The calculated available fault current at the primary side of the transformer on the third floor is approximately 60kaic. We have a disconnect switch on the primary side of this 3rd floor transformer. Question, is the disconnect required to be fused to meet the AIC rating of the circuit it's on? My understanding is that an unfused disconnect is only rated 10kaic. The answer seem to be obviously Yes you need a fuse, but I'm receiving some push back. We meet the OCPD for the transformer from the breaker, but if a fault occurs it could potentially damage that disconnect. Am I missing something?