Fused disconnect required.

Status
Not open for further replies.

dinkelja

Member
I have a generator with a 400 A main circuit breaker that feeds a service disconnect located within 30 feet of a mobile office. The service disconnect feeds the panelboard in the mobile that has a 100 A main circuit breaker. No 1 AWG is used from the generator to the service disconnect (outside tap rule), and from the service disconnect to the panelboard. Can the service disconnect be non-fused?
Thanks in advance.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If, in fact, the disconnect is to be considered the Service Disconnect then
230.91 requires the OCP be integral with or immediately adjacent to the disconnect.
Is the transformer a power company transformer ?
 