For multimotor circuits, wire sizes are to be 125% of the largest load plus all other loads. Where multiple loads are present, how is each fused disconnect sized? For example, if two roof top units each need 50A fuses, code would allow them to be placed on a single circuit with the breaker and wire sized properly. I understand how to size the wire and breaker, but I'm not sure how to size the disconnects. Would 60A disconnects be adequate if the circuit is fed from a 90A breaker? That is what I get when reading 2008 NEC 440.12.B and 430.110. It says the disconnecting means must be sized for all simultaneous loads. Since each disconnect will only carry the load of a single RTU, wouldn't a 60A disconnect be adequate? I'm assuming that the disconnect would be fed from a junction box (i.e., a tap) so that only the current from a single RTU passes through the disconnect.