• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Fused disconnect switch

anbm

Senior Member
Location
TX
Occupation
Designer
What is the reason to use fused disconnect switch ahead of a motor or an appliance in lieu of a none-fused disconnect switch?
Is it code? I thought the breaker in electrical panel will protect the load from overload and short circuit already?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Yes a CB will, but a dual element time delay fuse can be sized smaller than a cb.
A few HVAC condensers require fused protection per the mfg
Sometime what’s installed for disconnect is what’s on the truck
 

JoeStillman

Senior Member
Location
West Chester, PA
Non-fused switches are only rated for 10 kAIC. Put a fuse in it and you can jump right up to 100 k. The rating can also be achieved by matching the manufacturer of the upstream breaker, but sometimes you can't. It makes fusing a no-brainer when there is high available fault current. You can almost always skip the calculation and get by with fuses.
 

anbm

Senior Member
Location
TX
Occupation
Designer
Non-fused switches are only rated for 10 kAIC. Put a fuse in it and you can jump right up to 100 k. The rating can also be achieved by matching the manufacturer of the upstream breaker, but sometimes you can't. It makes fusing a no-brainer when there is high available fault current. You can almost always skip the calculation and get by with fuses.
Great point. Thank you.
 

milmat1

"It Can't Do That !"
Location
Siler City, NC USA
Occupation
Controls Engineer
In a control panel I typically place a fused J-class disconnect, then each branch motor circuit is protected by it's own MPCB.

If it is only a single motor circuit, the high SCCR is likely why. And a dual element TD fuse is the best protection for a motor circuit IMO.
 
Top