mshields
Senior Member
- Location
- Boston, MA
If you are feeding a motor, lets say a 30HP motor @ 480V. And lets say you're using a FVNR motor starter (which you don't don't see alot of these days but lets just say). You run a feeder that is 125% of the FLA and you use a 100A circuit breaker (i.e. 250%). At the motor, concerned about fault current you provide a fused disconnect. What size fuse would you provide.
I would only be providing the fuse to give the disconnect a withstand rating larger than the 7kA or so they are rated for without the fuse. Still you want to make sure that the fuse doesn't go before the breaker. It seem obvious to me that you'd need a 100AS/100AF.
Do you agree?
If it's a drive (clearly more likely in this day and age), then I would go with 50A wire, a 50A Circuit breaker and a 60AS/50AF. It seems to me that we should be running more motor circuits like this. For some reason, our standard is to provide breakers that are typically 175% of FLA. You end up need to have a 100AS rather than the 60A you ought to be able to use.
I would only be providing the fuse to give the disconnect a withstand rating larger than the 7kA or so they are rated for without the fuse. Still you want to make sure that the fuse doesn't go before the breaker. It seem obvious to me that you'd need a 100AS/100AF.
Do you agree?
If it's a drive (clearly more likely in this day and age), then I would go with 50A wire, a 50A Circuit breaker and a 60AS/50AF. It seems to me that we should be running more motor circuits like this. For some reason, our standard is to provide breakers that are typically 175% of FLA. You end up need to have a 100AS rather than the 60A you ought to be able to use.