I have a 400' aerial pole line that now runs from the Service Point (on a private utility pole, one span in from the utility company pole) and then to the existing building. I want to protect this triplex cable since it runs through large trees and i don't want a short or ground fault caused by a downed tree or broken limb to damage or destroy the aerial feeder. The building has an existing service disconnect typically located immediately inside the outer wall of the building. Section 230.82 (1) allows "current limiting devices" to be installed ahead of the service disconnect. To me a fused disconnect certainly meets the criteria of a current limiting device, but a local "code expert" I discussed this with tells me 230.82(1) is not applicable here. He says that if I want to add the fused disconnect near the street, it must become the new service disconnect. He claims that the first disconnect on the premisies MUST be the service disconnect. If I make the disconnect on the pole the service disconnect, I would need to carry the additional grounding conductor and also run my grounding electrode conductor 400' to the pole mounted disconnect. My grounding electrode will now be 400' from the building, in my view not desireable in case of a lightning strike or a ground fault. To me situations like this are exactly why 230.82(1) was written.What do you think?