Hi, an Arch/Engineering Firm has drawn a riser diagram with a Transformer feeding an 800amp CT Cabinet. Then dispersing 200amps to each of 4 separately metered tenants. According to the 02 NEC 230.40 Ex 1 this is ok.
Then they go on to include installation of 200amp FUSED DISCONNECTs between the meters and a 42 ckt Panels. My design intent (in order to save the cost of the disco,fuses,pipe,wire,and labor ect.) would be to eliminate the fused disconnect and purchase 42 ckt. panels with 200amp MAIN BREAKERs for each location. According to the 02 NEC 230.90(A)ex.2 this is code compliant or am I reading more into it than I think?
Thanks, thought I'd check with the Pro's before inserting foot in mouth. Mike
Then they go on to include installation of 200amp FUSED DISCONNECTs between the meters and a 42 ckt Panels. My design intent (in order to save the cost of the disco,fuses,pipe,wire,and labor ect.) would be to eliminate the fused disconnect and purchase 42 ckt. panels with 200amp MAIN BREAKERs for each location. According to the 02 NEC 230.90(A)ex.2 this is code compliant or am I reading more into it than I think?
Thanks, thought I'd check with the Pro's before inserting foot in mouth. Mike