Off the top of my head, four things come to mind:
Does the downstream equipment require fuse protection.
Are fuses required to address fault currents.
Will a NF disconnect comply with Code (see this ongoing thread: http://forums.mikeholt.com/showthread.php?t=179232 )
Often times if the exact size of the protection is not known (such as HVAC units where exact specs are not provided at initial wiring)
some folks use fusible disconnects as its easier to select the correct fuse than change an existing breaker if necessary)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the drawing simply shows a piece of equipment with a symbol for a disconnect I would assume that it's non-fused.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The schematic symbols are pretty distinctive from each other. What are you looking at that has them not shown correctly.
I don't disagree, but I have seen a LOT of very lazy drafting jobs make it to project specs.

Case in point: All of these are using the symbol for a NF Disconnect, yet clearly, they are not. Luckily, they are labeled...
maxresdefault.jpg
 
Last edited:

mstrlucky74

Senior Member
Location
NJ
The schematic symbols are pretty distinctive from each other. What are you looking at that has them not shown correctly.

Yes they usually are..not in this situation. Its a disconnect for a industrial type washing machine(tunnel washer)...60a 480v
 

Ingenieur

Senior Member
Location
Earth
I don't disagree, but I have seen a LOT of very lazy drafting jobs make it to project specs.

Case in point: All of these are using the symbol for a NF Disconnect, yet clearly, they are not. Luckily, they are labeled...
View attachment 15772

I've seen it depicted like that (or like a set of schematic relay contacts) if it is a vacuum or air contactor/switch controlled by external protective relaying
 