Fused & Unfused Conductors

Status
Not open for further replies.
Does the NEC allow Fused & Unfused Conductors in a Service Wireway?

Good question. The NEC says you can't have service conductors in the in the same "raceway" as feeders and branch circuits (don't have a code book with me, so I can't say the exact art.) Is a wireway considered a raceway?
In any event, IMHO, it is a very poor practice and I would not allow it on a job that I had control over. Also be aware that many POCOs will not allow it and I have seen a fair number of AHJs that won't allow it either.
 
Good question. The NEC says you can't have service conductors in the in the same "raceway" as feeders and branch circuits (don't have a code book with me, so I can't say the exact art.) Is a wireway considered a raceway?
In any event, IMHO, it is a very poor practice and I would not allow it on a job that I had control over. Also be aware that many POCOs will not allow it and I have seen a fair number of AHJs that won't allow it either.

Art 100:
Raceway. An enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or
busbars, with additional functions as permitted in this Code. Raceways include, but are not limited to, rigid metal
conduit, rigid nonmetallic conduit, intermediate metal conduit, liquidtight flexible conduit, flexible metallic tubing,
flexible metal conduit, electrical nonmetallic tubing, electrical metallic tubing, underfloor raceways, cellular concrete
floor raceways, cellular metal floor raceways,
surface raceways, wireways, and busways.
 