Fused/Unfused in Trough

Status
Not open for further replies.

am1954

Member
Location
NY
Occupation
contractor
Hey all,
We have a scenario where we want to do our interconnection inside a trough located below the building's service disconnect. Due to odd layout of equipment/conduit the trough would end up containing: 1. PV Service Conductors 2. Building Service Conductors 3. The fused feeders from the loadside of the buildings disconnect. So a set of fused feeders in the same trough as un-fused service conductors Think there is anyway we can justify that or no? Thanks for any thoughts...
 
Would this apply to your situation ?
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable in which the service conductors are installed
 