the question is in installing heat pumps, whether or not the service disconnects need to be fused. The heat pumps are 208/3ph, 208/1ph, and 460/3ph.
 

BAHTAH

Senior Member
Location
United States
Re: fused vs. non-fused disconnects

Denny, if the branch circuit overcurrent protection supplying the unit meets the requirements for protection then you can use a non-fused disconnect. Example would be if you have fusible distribution feeding the HVAC unit and the unit called for fuse protection there would be no reason to have fuses protecting fuses on the same circuit so you would install a non-fused disconnect at the unit.
 

ron

Senior Member
Re: fused vs. non-fused disconnects

Also double check the available short circuit current at the disconnects. If it will be more than 5000A (generally the withstand rating of a unfused switch), then use a fused switch even if the equipment nameplate doesn't require it.
Usually on a small unit, the small wire size leading to the unit will reduce the short circuit avaiable below 5KA.
 