Don't know the answer to exactly what you asked.
What I do know is that with the SCR control, it may no longer act like a clean resistive load. With the SCR constantly chopping the sinewave, the load will be very noisy, and without substantial filtering to reduce harmonics, the branch circuit, conductors, breakers, will just run a lot warmer than you expect. Seen it before, surprisingly so, with SCR controlled heating elements. Oversized conduits and panels running much warmer.
So, if your question was if you should expect nuisance tripping, the fuses will not like constantly running warm.
Not quoting the code, I would have to look it up, but heating type appliances I would expect are continuous loads, so the source would be at 125%. Not sure if you are trying to use the exception for 100% rated equipment.